Troubleshooting
Make a Servo Jog Follow a Joystick Velocity Demand
A velocity jog reads its speed operand only when the instruction executes, so a running jog ignores the joystick value until you re-execute it. Strobe the jog every scan with the scaled stick velocity and keep a deadband at neutral; any lag left after that is the acceleration limit, not the command path.
Troubleshooting
Brushed DC Servo Tach Dropout Diagnosis: Why It Jumps
Jump at one shaft angle plus a speed-synchronous lope after tach work is a dropout in the tach's voltage, not an encoder or alignment fault. Prove it by spinning the feedback shaft and looking for a once-per-revolution notch in tach voltage; a cracked armature conductor needs a replacement armature or feedback unit, not another coat of insulating varnish.
Troubleshooting
How to Tell if a Servo Motor Is Actually Faulty
A servo motor is only confirmed faulty when it still fails with a known-good drive, verified feedback, and the load uncoupled. Read the commanded motion, the measured motion, and the motor current during the same event: high current with no movement points to the load or the feedback, and no command with no movement points upstream of the motor.
Troubleshooting
Why a Servo Motor Oscillates Between Two Positions
A servo that hunts in a stable 30-50 degree band and restarts on a light shaft nudge has a working position loop running on wrong motor or load data. Fix the configuration — engineering units, load description, pole count, resolver excitation — before swapping phases or retuning: in the documented case, converting metric values into the drive's lbf-ft fields and correcting the load entry stopped it.
Selection guide
Choosing Servo or Stepper for a 1% Speed Regulation Pinch Wheel
Pick the servo: behind a 45:1 planetary reducer, a velocity-mode servo meets a 1% wheel-speed tolerance with margin, because 200-300 lb-in at 80 rpm needs only 4.9-7.4 lb-in at the motor and the loop corrects load-induced error. A stepper qualifies only when its torque-speed curve clears the load with margin at the required motor speed and a measured ripple test holds the wheel inside 0.8 rpm.
How-to
Match a Stepper Feed Rate to Conveyor Speed With an Encoder
Continuously scale the conveyor encoder's measured count rate into the pulse-output velocity register: divide the count rate by the counts per inch of belt travel, then multiply by the label-feed ratio and the drive's pulses per inch of label travel. A fixed feed rate matches one belt speed only; the per-scan register update is what makes the labeler follow the belt.
How-to
Following a Master Axis With a Stepper Traverse
Gear the traverse stepper to measured spool rotation, not to a fixed speed ratio: commanded traverse speed is v_t = p × n_s, so pitch stays constant as the spool fills. The follower ratio comes from pitch, screw lead and drive resolution — 25 step pulses per 64 master counts in the worked example — and master acceleration must be limited so the amplified slave ramp cannot stall the open-loop stepper.